Bolted Joints between Steel Beams and Reinforced Concrete Columns

  Steel Beams.pdf (Size: 708.81 KB / Downloads: 3)

Abstract

The steel beams to RC columns joint are usually done by welding the beam to a steel core within the column.

This solution is well covered in one of the Journal of Structural Engineering papers “Guidelines for Design of

Joints between Steel Beams and Reinforced Concrete Columns”. The same methodology is assumed in the

Romanian code “Cod de proiectare pentru structuri de beton armat cu armatura rigida” NP033-99. However,

in case that a contractor avoids using on-site welding due to various difficulties, and a continuous steel beam

through the reinforced concrete column is still required, a bolted connection between the beam and the inner

steel core should be considered. This paper presents an extension of these guidelines to a bolted connection

type. A nonlinear finite element analysis with proper definition of contact relationships between components is

performed in order to assess the role of each principal contributor (i.e. steel panel, inner concrete and outer

concrete regions).

Introduction

Shear strength in RCS (reinforced concrete steel) connections is provided by three mechanisms: steel web

panel, inner diagonal concrete strut and outer diagonal concrete strut.

1. Steel web panel. In RCS connections the behaviour of the steel web panel is similar to that in steel

frames.

2. Inner concrete. The inner diagonal concrete strut is activated through bearing of the concrete on the

steel beam flanges and face bearing plates welded between the beam flanges at the column faces.

3. Outer concrete region. The horizontal concrete struts are mobilized through extended face bearing plates

(FBP) or steel column, above and below the steel beam – these struts may be separated into twocomponents: one parallel to the beam and one perpendicular. Those perpendiculars are selfequilibrating and those parallel to the beam are sent further to the outer compression field. (seeFigure 8 of ref [1])

Joint Forces

The joint should be design for the interaction of forces transferred to the joint by adjacent members, including

bending shear and axial load.

The design forces as per ref. [1] do not include the effects of axial forces in the concrete column, and since

axial forces in the beams are usually small, these are also excluded from calculations. It is considered

conservative to neglect the effects of axial compressive loads normally encountered in design. Moreover, it is

predictable that the strength of the concrete joint mechanisms will be greater in joints where beam frame into

four, rather than two sides of the column, due to additional confinement.

Effective Joint Width

The joint shear strength is calculated based on an effective width of the concrete joint, which is the sum of the

inner and outer panel widths. The concrete in the inner panel is mobilized through bearing against the FBP

between the beam flanges. The participation of concrete outside of the beam flanges is dependent on

mobilization of the horizontal compression struts that form through direct bearing of the extended FBP on

the concrete above and below the joint.

Analysis Results

This section presents the analysis results from the finite element analysis of the connection. The stress

diagrams presented in the following Figures provides information in Mp/m2

• Figure 6 presents the crack distribution along with the compressive stress field in the inner joint

region. The thickness of the inner joint region (an implicitly the thickness of its finite plane-stress

elements) was considered equal to the beam flange width – 350mm. The maximum principal

compressive stress in the strut is roughly 20MPa. Two compressive diagonal struts were developed –

due to presence of the flange steel-column. The maximum bearing stress is already attained – but is

very localized and since the model disregarded the steel band plates this not represents a concern

(maximum strain is 4⋅10-3 which is acceptable in case of strong confinement provided by the steel

band plates above and below the steel beam).

Conclusions

The success of a connection design in terms of deformation and strength is directly related to the overall

behavior of the building. Apparently, for a regular concrete building this goal may be attain more easily, but for

a composite structure this may be challenging. The success of connection design (in terms of stiffness and

strength) directly affects the response of the building and implicitly the possibility to meet the target drift ratio,

therefore special care have to be provided to particular connection types, especially if they have not been

tested enough.